Author Topic: Help needed electrical Guru's for phase converter sizing  (Read 1326 times)

0 Members and 1 Guest are viewing this topic.

Billyisgr8

Help needed electrical Guru's for phase converter sizing
« on: November 25, 2009, 05:30:40 PM »
Purchasing a 220volt  3 phase machine that runs at 23 amps 3 phase.....I have single phase 220 in my shop.......what size phase converter is needed to run this on 220 volt single phase.   I'm not finding any calculators on line for this.

Kevin

Offline Mirko

  • *
  • Posts: 153
  • Karma: 1
  • dude, where's my car?
Re: Help needed electrical Guru's for phase converter sizing
« Reply #1 on: November 25, 2009, 07:47:42 PM »
I think you need a phase converter that will match the HP of the motor you are converting.
23 amps on three phase.. thats a big motor! I'm guessing 10 to 15 HP?? what kind of machine is it?

Last machine I did, I used a static/electronic phase converter for a 2HP motor and it cost 400 bucks!!
In some cases its cheaper to change out the motor.

Good luck.
« Last Edit: November 25, 2009, 07:55:24 PM by Mirko »


"Perfection is achieved, not when there is nothing more to add, but when there is nothing left to take away."

Billyisgr8

Re: Help needed electrical Guru's for phase converter sizing
« Reply #2 on: November 25, 2009, 08:00:44 PM »
Its one machine with a combination of  4 motors.  The amp rating is off the main machine id plate so thats what I have to go by.  It  has one 5hp, and 3 - 1hp motors

Kevin

Offline Mirko

  • *
  • Posts: 153
  • Karma: 1
  • dude, where's my car?
Re: Help needed electrical Guru's for phase converter sizing
« Reply #3 on: November 25, 2009, 08:14:25 PM »
http://www.grizzly.com/products/searchresults.aspx?q=converter

Have a look at this.

From their site:
(On heavily loaded or hard-start applications, such as high-speed geared-head lathes and air conditioning compressors, the nameplate rating of the converter you choose should be 2 to 3 times the HP of the most heavily loaded motor. For application assistance, please call our technical support group at (570) 546-9663.)
« Last Edit: November 25, 2009, 08:18:27 PM by Mirko »


"Perfection is achieved, not when there is nothing more to add, but when there is nothing left to take away."

Offline Mowser

  • "You know, Hobbes, some days even my lucky rocketship underpants don't help. " Calvin
  • *
  • Posts: 1292
  • Karma: 1
Re: Help needed electrical Guru's for phase converter sizing
« Reply #4 on: November 25, 2009, 08:21:44 PM »
Gee, who do you know that could possibly help you out with that.... or perhaps even stop by and look at it in person.  Nope, I got nuttin'  Give me a call ya shmuck.